FabianLT Jul 2, 2015 04:43 PM

We are running an Eddy Covariance system at a remote place in Peruvian Amazon, until now we were using a 2gb CFMC but we are going to swich to 16Gb CFMC. Our system works with a CR3000 equiped with a CFM100 and the program is running with the "CardOut" instruction (0,-1). I was reading that it might be better to use the "TableFile" instruction. Do I really need to do this? Can I keep the CardOut instruction instead?

Thanks!


JDavis Jul 6, 2015 06:19 PM

CardOut can be used with 16GB cards, but you might not use the full space of the card. CardOut is limited to 2GB per table. So, if you have 4 data tables and only use CardOut, you would only use 8GB of the card. TableFile is limited to 2GB per file, but can divide data from a table into multiple files. TableFile can use the entire 16GB of space on the card.

TableFile also has some usability advantages.

I strongly suggest you follow the guidance in our application note about using large cards:
https://s.campbellsci.com/documents/us/technical-papers/write-high-frequency-data-to-cf-cards.pdf


FabianLT Jul 7, 2015 12:24 AM

Thanks!

I'm following that guidance, that is why I was thinking on reaplace the CardOut instruction. When I set the file name, lets say "CRD:TamboFlux" it turns pink, is that correct? I did compile the program and there was no error reported. I wrote:

TableFile ("CRD:TamboFlux",64,-1,0,0,Hr,0,0)

"CRD:TamboFlux" is on pink,
64 because I want to use that option,
-1 no limits
0 no intervals, I want to write everything I can
0 same, no intervals.
Hr
0 no using OutStat
0 no using LastFileName

Am I doing it right?