Our full technical support staff does not monitor this forum. If you need assistance from a member of our staff, please submit your question from the Ask a Question page.


Log in or register to post/reply in the forum.

Vaisala WXT520 Weather Transmitter and CR850


Monitoring Nov 26, 2014 07:08 AM

Hi,

Currently i am using Vaisala WXT520 Weather Transmitter, and when i view the rain and hail reading of the WXT520 via vaisala configuration tool software (laptop), i noticed that the reading for rain and hail showed "missing" but the rest of the reading such as windspeed, wind direction, barometer all are looking fine.

In my actual set up, wxt is connected to cr850 via SDI12. I noticed that the reading of rain and hail is keep showing zero although there is raining day.

May i know what is the problem?

Thank You

* Last updated by: Monitoring on 11/26/2014 @ 12:10 AM *


smile Nov 28, 2014 09:36 PM

Hi

try reading the manual campbell, to see if you can find useful information
link s.campbellsci.com/documents/us/manuals/wxt520.pdf

Smile


JDavis Dec 1, 2014 06:03 PM

The precipitation readings from the sensor zero out between readings. In other words, the readings for precipitation show how much precipitation fell within a scan interval. You should use Totalize within a data table to add up the individual rainfall measurements throughout the day, and our daily total will be correct.

Log in or register to post/reply in the forum.