Need to Create a Timestamp at the Beginning of the Averaging Interval


MonSr Dec 27, 2013 08:56 PM

Currently, our data tables are being timestamped with the time that the record is generated. We would like a timestamp (can be a second 'dummy' timestamp column) that would reflect the time that the averaging interval started. Any ideas? We are trying to avoid doing this post-processing and would prefer it to show in the data tables.


Danaw Jan 9, 2014 04:51 PM

Newer OSes have a DataTime instruction. I am not sure if this will help, as what you report above seems to be different than what should be happening. However, take a look and see if it helps.

I suspect you could also use the RealTime instruction to store into a variable at the time of the measurement and then store that variable to the data table.

Dana


Danaw Jan 9, 2014 04:54 PM

Or perhaps rather than Real-Time, you may be able to use Status.timestamp, but now that I think about it, this and the RealTime instruction may report time at the beginning of the scan... you'll just need to check it as I am answering off the top of my head!

Refer to the data table access topic in the CRBasic help for additional information on using Status.Timestamp.

Dana


MonSr Jan 9, 2014 05:26 PM

Dana,

Thank you for the follow up. We did end up creating a second timestamp column in each data table using TableName.TimeStamp which does timestamp at the beginning of the data record. I don't have access to a logger for testing to try the DataTime instruction.

Public PTemp, batt_volt, StartTime As String *32

DataTable (Test,1,-1)
DataInterval (0,60,Sec,10)
Sample (1,StartTime,String)
EndTable

BeginProg
Scan (1,Sec,0,0)
StartTime=Test.TimeStamp(1,1)
PanelTemp (PTemp,250)
Battery (batt_volt)
CallTable test
NextScan
EndProg